请问地上地下共用室外疏散楼梯,其室外疏散楼梯在首层是否需要完全分隔?

请问地上地下共用室外疏散楼梯,其室外疏散楼梯在首层是否需要完全分隔?

weiwei6217 | 2024-08-06 12:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

LHH2737 2024-08-06 15:04 00 [回复]举报

通规7.1.10.3条:地下楼层的疏散楼梯间与地上楼层的疏散楼梯间,应在直通室外地面的楼层采用耐火极限不低于2.00h且无开口的防火隔墙分隔;

地下室怎么使用室外疏散楼梯进行疏散,这个很奇怪

phone0224 2024-08-09 09:18 00 [回复]举报

又是一个创新的设计,规范肯定没有具体的条文来规定这个做法是否可行,但是从通规7.1.10-3的条文说明可知,楼梯间的地上层和地下层连接处需合理分隔,以有效防止疏散人员误入地上楼层或地下楼梯。为什么会误入,因为在楼梯间里面疏散不知道自己跑到第几层了,但是你如果是室外疏散楼梯,我觉得误入的概率基本不太有。所以应该是不需要做分隔的。

以上仅个人理解。