消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

电影院内排烟

我区有一个很小的电影院,在商场一层设置的电影院,总面积200平米多一点,共两个放映厅,每个76平米。

问:建筑防火通用规范8.2.2第六项还是8.2.5,依据这两条哪个规范来要求,是否需要设置排烟?


因为看了2018版建规,发现电影院不属于歌舞娱乐放映游艺场所。。。。。无奈是不是要按照建筑防火通用规范8.2.5来要求电影院设置排烟?我们这个电影院太小了,设置个排烟赶紧没必要啊。。。。

一红到底 | 2023-09-12 10:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

张治福 2023-09-13 11:47 01 [回复]举报

8.2.5是对前列规范条款的补充。是对无可开启外窗的房间或区域。


如果你这两个放映厅无可开启外窗条件,那就必须要设置排烟(机械排烟)。

如果这两个放映厅可以开设外窗,那就开设外窗即可(默认开设的外窗可以做通风排烟使用)

陈曲 2023-09-13 11:53 00 [回复]举报

这个得按公共建筑内建筑面积大于100㎡且经常有人停留的房间必须有排烟(可以是自然排烟) 又因为是无窗房间所以必须设置机械排烟

阳明心   回复: 陈曲2023-09-14 08:40

陈曲老师,但他的每个放映厅的面积是76㎡,小于100㎡,还适用"公共建筑内建筑面积大于100㎡且经常有人停留的房间必须有排烟"吗

0    0 [回复]举报

陈曲   回复: 阳明心2023-09-21 12:47

如果有窗 且可以开启那就都不是问题了 如果不可开启 就适用50平的无窗房间 要设机械排烟

0    0 [回复]举报

whale 2023-09-13 17:37 00 [回复]举报

建筑设计防火规范GB50016-2014(2018年版)中规定了需要设置排烟的场所。

关于地上建筑面积大于50平小于100平规范中没规定,我们这边设计中执行的是这种房间设置有可开启外窗就行,不对面积和开启高度进行要求。

具体怎么做可以和审图单位沟通一下。

潘天坤 2024-06-20 00:45 00 [回复]举报

两个70多平方米的放映厅有可开启外窗嘛?

建筑面积大于50平方米且经常有人停留的无可开启外窗的房间应设置排烟设施

关闭

关闭

手机APP下载