消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

银行一楼营业厅二楼办公,是执行办公楼?

银行营业厅一楼700平米是营业厅,二楼为办公室600平米,是否用设室内消火栓?

| 2022-03-24 17:54
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

充楞装傻 2022-03-25 10:56 00 [回复]举报

独立建筑,按照建规8.2.1不需要。

否则按照 消水规 7.4.3 设置室内消火栓的建筑,包括设备层在内的各层均应设置消火栓。

法亦有道 2022-03-25 12:07 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版) 第8.2.1条建筑高度大于 15m 或体积大于 10000m³ 的办公建筑、教学建筑和其他单、多层民用建筑应设置室内消火栓系统

石小东 2022-03-25 14:06 00 [回复]举报

1.对于银行的金库,按照《银行金库》 JR/T0003-2000,5.5 消防系统:除安装火警报警设备外,库房内不设其它消防设施。库区应按照《消防法》的规定,配备消火栓等有关防火设施。

2.对于营业厅和办公场所,按照建筑设计防火规范 GB50016-2014(2018年版)8.2.1 下列建筑或场所应设置室内消火栓系统: 5 .建筑高度大于 15m 或体积大于 10000m³ 的办公建筑、教学建筑和其他单、多层民用建筑。

具体要看你们银行是否在建筑高度大于15米或体积大于1万平的建筑内。

9527 2022-03-26 15:00 00 [回复]举报

按照建规8.2.1条,此独立建筑不需要设置室内消火栓,但银行的营业厅属于人员密集场所,应该设置消防软管卷盘或轻便水龙。

关闭

关闭

手机APP下载