暖通系统的防火阀要不要装模块

前提是场所是自然通风、自然排烟,这个场所有一些房间有通风设备、防火阀,防火阀需要装模块接入主机吗?

王发发 | 2025-02-13 08:01
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0

回答 | 3

潘天坤 2025-02-13 14:24 10 [回复]举报

楼主说的是设备房排风系统穿越防火隔墙设置的防火阀嘛?

一般来说,如果不属于防烟、排烟及与防排烟系统合用的通风空调系统,一般不需要设置信号反馈


工业建筑供暖通风与空气调节设计规范 GB50019-2015第11.1.12条规定:
防火与排烟系统的监测与控制应符合现行国家标准《火灾自动报警系统设计规范》GB 50116的有关规定;兼作防排烟用的通风空气调节设备应受消防系统的控制,并应在火灾时能切换到消防控制状态;风管上的防火阀宜设置位置信号反馈


民用建筑供暖通风与空气调节设计规范 GB50736-2012 第9.1.7条规定:
防排烟系统的检测与监控,应执行国家现行有关防火规范的规定;与防排烟系统合用的通风空调系统应按消防设置的要求供电,并在火灾时转入火灾控制状态;通风空调风道上的防火阀宜具有位置反馈功能


民用建筑电气设计标准 GB51348-2019第13.4.4条规定:
防烟、排烟设施的联动控制设计应符合下列规定:6 设于空调通风管道出口的防火阀,应采用定温保护装置,并应在风温达到70℃时直接动作,阀门关闭;关闭信号应反馈至消防控制室,并应停止相关部位空调机组