储烟仓的厚度和最低清晰高度二者无法同时满足怎么取舍

建筑防烟排烟系统技术标准 GB51251-2017 中,当室内空间无法同时满足4.6.2储烟仓厚度和4.6.9最小清晰高度时怎么处理,如室内吊顶的高度为2.3m时,储烟仓厚度最小0.5m,而最小清晰高度1.83m,1.5+1.83=2.33大于2.3m.

雄哥 | 2025-01-24 11:14
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 11

LHH2737 2025-01-24 15:42 00 [回复]举报

解决不了,一定会有一个不满足,应按设计清晰高度考虑,不应低于2.1m

徐海金 2025-01-24 16:24 00 [回复]举报

2.3米,确定不是夹层或吊顶?这么奇葩建筑?

雄哥   回复: 徐海金2025-02-05 09:24

通道吊顶净高

0    0 [回复]举报

雄哥   回复: 徐海金2025-02-05 09:25

吊顶后净高

0    0 [回复]举报

大谧   回复: 徐海金2025-03-18 14:38

净高低于2.6米就应该警觉排烟的问题

0    0 [回复]举报

潘天坤 2025-01-24 21:01 20 [回复]举报

空间净高2.3为小于3米的场所,清晰高度为净高的二分之一,即为1.15米

不过也存在个问题,相关规范有疏散通道净高2.1米的要求,2.3米的净高确实存在问题,可能要考虑设置门、实体墙、通透性大于25%的吊顶等方式解决

南明离火   回复: 潘天坤2025-01-25 08:49

0    0 [回复]举报

雄哥   回复: 潘天坤2025-02-05 16:08

疏散通道净高不小于2.1M,我并未查到相关规范条文,仅在 建筑设计防火规范 GB50016-2014(2018年版)城市交通隧道中有明确要求。

0    0 [回复]举报

潘天坤   回复: 雄哥2025-02-05 17:49

民用建筑很多本规范及建筑防火通用规范中都有相关净高要求的描述





0    0 [回复]举报

单车恋人   回复: 雄哥2025-02-19 10:59

新的通用规范里明确了疏散门的净高,而不是走道的净高!一般来说设计以门的最小高度来确定确定清晰高度!也就是说现在最小清晰高度不能低于2.1米,之前是最低2.0米。你这个吊顶确实太低了!最低要做到2.65米才能满足储烟仓和最小清晰高度的要求。

0    0 [回复]举报

PQ 2025-02-06 14:15 00 [回复]举报

按4.6.9条,走道的最小清晰高度不宜小于其净高的1/2即可。但2.3米净高无法设置挡烟垂壁,挡烟垂壁下端距地不应小于2.1米,以符合建筑防火通用规范的要求。如果需要划分防烟分区,则可考虑更改为通透型吊顶。