消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

防火管井门,强.弱电井门是否需要安装闭门器.顺序器?

管井门规格在800*2000以内,强电弱电井规格在1200*2000以内的是否需要安装闭门器。及顺序器?

金懂你 | 2024-10-26 10:01
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

japan03126 2024-10-27 07:38 00 [回复]举报

不需要,一般这些地方都是严管区域,长期保持关闭,没有钥匙都进不去。

懒得说 2024-10-27 08:33 00 [回复]举报

不需要闭门器。不是作为通道考虑

阿童木木 2024-10-27 11:14 00 [回复]举报

除管井检修门和住宅的户门外,防火门应具有自行关闭功能。双扇防火门应具有按顺序自行关闭的功能---建筑设计防火规范 GB50016-2014(2018年版)6.5.1.3,故不需要安装

关闭

关闭

手机APP下载