无人值守配电间需要做消防应急照明吗

根据规范,配电室等发生火灾时仍需工作、值守的区域应同时设置备用照明、疏散照明和疏散指示标志。如果时无人值守配电间,而且发生火灾时无需人值守工作(无消防设备,其他建筑的应急照明带蓄电池),是不是这些都不用设?

然后配电间设置的备用照明就不属于消防应急照明(维修备用),是否可以不按《消防应急照明和疏散指示系统技术标准》(GB51309-2018)的3.8.2的备用照明要求设置?

xie00 | 2024-08-28 14:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

破忒头 2024-08-29 09:27 00 [回复]举报



潘天坤 2024-08-30 13:29 10 [回复]举报

1、发生火灾时无需工作和值守的配电室可以不需要设置疏散照明和疏散指示标志(消防应急照明和疏散指示系统技术标准 GB51309-2018),但是要考虑一种情况:如果属于设置气体灭火场所,可能还要满足“防护区内的疏散通道及出口,应设应急照明与疏散指示标志”要求


2、备用照明除了GB51309消防应急照明和疏散指示系统技术标准提到之外,还有挺多规范(GB50016建规、GB55307建筑防火通用规范、GB51348民用建筑电气设计标准 )均有提及:配电室应设备用照明(这边没有是否值守的前缀),个人觉得应按照相关规范要求执行,建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准
上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

xie00   回复: 潘天坤2024-08-30 18:07

我没说不用做备用照明,只是确实这个情况下备用照明是否可以不按《消防应急照明和疏散指示系统技术标准》(GB51309-2018)的3.8.2的备用照明要求设置

0    0 [回复]举报

潘天坤   回复: xie002024-09-02 09:07

请问具体是哪些要求,可以展开说说嘛

属于备用照明的话,理论上还是得遵循这个条文


0    0 [回复]举报

xie00   回复: 潘天坤2024-09-03 15:10

主要是这条2 备用照明灯具应由正常照明电源和消防电源专用应急回路互投后供电。消防电源专用应急回路互投,因为其他建筑消防应急照明用的三级负荷,消防应急配电箱电源由照明回路引出,备用照明想自带蓄电池或利用工业UPS柜单回路