消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问麻将馆属于歌舞娱乐放映游艺场所吗?400平方米的麻将馆需要设置报警系统吗?

请问麻将馆属于歌舞娱乐放映游艺场所吗?400平方米的麻将馆需要设置报警系统吗?

| 2024-06-16 18:02
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

潘天坤 2024-06-16 23:10 10 [回复]举报

防火通用规范和建规条文说明提及的“歌舞娱乐放映游艺场所”包括歌厅、舞厅、录像厅、夜总会、卡拉OK厅和具有卡拉OK功能的餐厅或包房、各类游艺厅、桑拿浴室的休息室和具有桑拿服务功能的客房、网吧等场所,不包括电影院和剧场的观众厅。 

麻将馆应该属于棋牌室类型,如果没有设置桑拿服务功能和卡拉OK功能都包房,应该不属于“歌舞娱乐放映游艺场所”,可能偏向于公共娱乐场所,属于消防法规定的人员密集场所。

是否需要设置,需要看是否设置在一类高层公共建筑里,是否设置机械排烟、防烟系统,雨淋或预作用自动喷水灭火系统,固定消防水炮灭火系统、气体灭火系统等需与火灾自动报警系统联锁动作的场所或部位。

如果都不属于,那么可以不设置火灾自动报警系统。

黄-江西省景德镇市 2024-06-17 02:29 00 [回复]举报

棋牌室属于公共娱乐场所,不可按歌舞娱乐放映游艺场所归类,400m²麻将馆不需要设置火灾自动报警系统,若麻将馆所属建筑原本就设置了的消防设施系统均应保留并做相应调整。不过即便原来没有报警,通常消防部门会让做,可装独立式火灾探测器。

懒得说 2024-06-17 07:59 00 [回复]举报

属于娱乐场所。需要设置FAS


-梧桐树 2024-06-17 08:23 00 [回复]举报

8.3.2 下列民用建筑或场所应设置火灾自动报警系统:     1 商店建筑、展览建筑、财贸金融建筑、客运和货运建筑等类似用途的建筑;     2 旅馆建筑;     3 建筑高度大于100m的住宅建筑;     4 图书或文物的珍藏库,每座藏书超过50万册的图书馆,重要的档案馆;     5 地市级及以上广播电视建筑、邮政建筑、电信建筑,城市或区域性电力、交通和防灾等指挥调度建筑;     6 特等、甲等剧场,座位数超过1500个的其他等级的剧场或电影院,座位数超过2000个的会堂或礼堂,座位数超过3000个的体育馆;     7 疗养院的病房楼,床位数不少于100张的医院的门诊楼、病房楼、手术部等;     8 托儿所、幼儿园,老年人照料设施,任一层建筑面积大于500㎡或总建筑面积大于1000㎡的其他儿童活动场所;     9 歌舞娱乐放映游艺场所;     10 其他二类高层公共建筑内建筑面积大于50㎡的可燃物品库房和建筑面积大于500㎡的商店营业厅,以及其他一类高层公共建筑。

香.香 2024-06-17 09:08 00 [回复]举报

麻将馆属于公共娱乐场所,至于是否需要设置自报还得看它所属的建筑类型。

一路同行 2024-06-17 10:15 00 [回复]举报

麻将馆不属于歌舞娱乐游艺场所,

关闭

关闭

手机APP下载