关于气体灭火剂浓度的相关问题

规范里提到的气体灭火剂灭火浓度需要达到的浓度是质量分数还是摩尔分数,查阅了很多文献,大部分是质量分数,也有写是质量分数的,做模拟出来确实是质量分数可满足,体积分数总是非常非常小。七氟丙烷的灭火浓度质量分数达到8%可以吗?

根据规范计算出来需要的七氟丙烷灭火剂的用量是126kg,根据质量守恒用模拟注入了126kg的气态的七氟丙烷,结果是质量分数满足,达到了设计浓度,摩尔分数差的非常远。

zzyzy | 2024-06-12 18:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

资源网小助理 2024-06-13 15:59 10 [回复]举报

用8%的浓度计算出来得到的是灭火剂的质量

zzyzy   回复: 资源网小助理2024-06-14 09:26

那就是灭火剂质量分数满足8%就达到灭火需求了,而不是体积分数?

0    0 [回复]举报

黄-江西省景德镇市 2024-06-15 21:53 00 [回复]举报

《气体灭火系统设计规范 GB50370-2005》2.1术语  中有相关诠释。灭火浓度即气体体积分数。