消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

在仓库里加了个一百平左右的钢平台,底下需要加喷淋和烟感吗?

大队长 | 2024-06-05 11:27
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

大队长 2024-06-05 11:47 00 [回复]举报

丙二仓

潘天坤 2024-06-05 12:27 00 [回复]举报

仓库原来是否有设置自动喷水灭火系统和火灾自动报警系统?

 根据以前建规及现行建筑防火通用规范关于自动灭火系统要求:除占地面积不大于2000平方米的单层棉花仓库外,每座占地面积大于1000平方米的棉、毛、丝、麻、化纤、毛皮及其制品的地上仓库,应设置自动灭火系统,并宜采用自动喷水灭火系统。

 根据以前建规及现行建筑防火通用规范关于火灾自动报警系统要求:每座占地面积大于1000平方米的棉、毛、丝、麻、化纤及其制品的仓库,占地面积大于500平方米或总建筑面积大于1000平方米的卷烟仓库应设置火灾自动报警系统。

安洪全 2024-06-05 14:22 10 [回复]举报

宽度超1.2米的管道下方都应增设喷头,这肯定得加


自动喷水灭火系统设计规范 GB50084-2017

冷风格   回复: 安洪全2024-06-12 15:10

同类问题,丁类车间,净空高度4米设置有下喷,在2米处有类似钢平台,下方是设备或者通道,需要设置吗?

0    0 [回复]举报

安洪全   回复: 冷风格2024-06-13 08:51

加了影不影响原设计,算不算障碍物,连宽度超1.2米的管道下面都要增设,如果是超过1.2米的加层底部同理应该增设。不因新增的使用功能削弱原有的灭火能力。

0    0 [回复]举报

一路同行 2024-06-05 14:50 00 [回复]举报

平台下方可以不设烟感,需要加喷淋(宽度超1.2米的管道下方应增设喷头

消防资源网 2024-06-05 14:58 00 [回复]举报

需要

南明离火   回复: 消防资源网2024-06-08 11:48

净空  8米,在净空2.5米处,有这种2米宽左右钢平台,下部是一体化自动设备,也需要设置吗,图纸没有,施工也不好做

0    0 [回复]举报

周家斌 2024-06-05 15:05 00 [回复]举报

需要的哦,这场面!

关闭

关闭

手机APP下载