消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

两个厂区消防水管网是否能够共用

大佬们。现在在做一个化工厂A,A厂区边上的厂区B现有消防水泵房,水罐有效容积等等都满足A厂区的要求。并且A/B厂同属于一个集团(但法人不同),两个厂区面积加起来不超过100公顷。消防联通管也确认可以穿两厂区中间市政道路。这种情况下两个厂区能否共用一套消防管网?

haikuowang | 2024-05-30 17:30
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

消防网友72300 2024-05-31 07:51 00 [回复]举报

必需可以啊,两个物业之间有协议即可

阳明心 2024-05-31 08:34 00 [回复]举报

可以的

周家斌 2024-05-31 08:40 10 [回复]举报

消防工程隶属于单位工程中各分部工程,从建设许可范畴来说,是很难的,在考虑供水半径、沿程阻力等技术满足要求的话,从技术上是可以的。

消防网友44826 2024-05-31 10:41 00 [回复]举报

《消防给水及消火栓系统技术规范》GB50974-201411.0.12 消防水泵控制柜应设置机械应急启泵功能,并应保证在控制柜内的控制线路发生故障时由有管理权限的人员在紧急时启动消防水泵。机械应急启动时,应确保消防水泵在报警后5.0min内正常工作。就是说能保证A厂区发生火灾,5分钟内B厂区有管理权限人员能将消防泵通过机械应急方式启泵。距离远管网长,无非就是启泵信号接收的比较慢,启泵时间比较长。但是厂区如果在发现泵控柜故障后(需要时间),再赶到泵房(又5分钟),而且化工厂一般不止有消火栓还有泡沫或者喷淋。这些系统的滞后,是否会造成化工火灾的扩大,需要楼主考虑。

南岳 2024-05-31 11:18 00 [回复]举报

如果水量、水压能同时满足两个厂要求,应该可以。

懒得说 2024-05-31 14:21 00 [回复]举报

室外消火栓满足覆盖半径可以共用。室内消火栓不建议共用


高山流水2024 2024-06-02 15:08 00 [回复]举报

两个厂区,应考虑2个起火点同时起火,因此,应考虑泵的额定流量、管网的管径、水池和水箱的容量等因素,符合条件才可以,否则应各建一套水系统。

关闭

关闭

手机APP下载