消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教一下高位水箱问题

高位水箱设于屋面,最不利点消火栓压力不小于0.07MPa,是否还需要设置稳压设施?

WeiHL | 2024-05-28 10:14
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

安洪全 2024-05-28 13:53 00 [回复]举报

看建筑规模和建筑性质

途安008 2024-05-28 14:02 00 [回复]举报

需要

消防检查 2024-05-28 14:13 00 [回复]举报

最不利点静压满足要求就可以不设增稳压设施。

消防网友68723 2024-05-28 15:03 20 [回复]举报

5.2.2 高位消防水箱的设置位置应高于其所服务的水灭火设施,且最低有效水位应满足水灭火设施最不利点处的静水压力,并应按下列规定确定:
    1 一类高层公共建筑,不应低于0.10MPa,但当建筑高度超过100m时,不应低于0.15MPa;
    2 高层住宅、二类高层公共建筑、多层公共建筑,不应低于0.07MPa,多层住宅不宜低于0.07MPa;
    3 工业建筑不应低于0.10MPa,当建筑体积小于20000m³时,不宜低于0.07MPa;
    4 自动喷水灭火系统等自动水灭火系统应根据喷头灭火需求压力确定,但最小不应小于0.10MPa;
    5 当高位消防水箱不能满足本条第1款~第4 款的静压要求时,应设稳压泵。

南明离火 2024-05-28 15:08 00 [回复]举报

 那就不用了

代号风筝 2024-05-28 16:00 10 [回复]举报

1 一类高层公共建筑,不应低于0.10MPa,但当建筑高度超过100m时,不应低于0.15MPa;
2 高层住宅、二类高层公共建筑、多层公共建筑,不应低于0.07MPa,多层住宅不宜低于0.07MPa;
3 工业建筑不应低于0.10MPa,当建筑体积小于20000m³时,不宜低于0.07MPa;

4 自动喷水灭火系统等自动水灭火系统应根据喷头灭火需求压力确定,但最小不应小于0.10MPa;
5 当高位消防水箱不能满足本条第1款~第4 款的静压要求时,应设稳压泵

倜圳 2024-05-28 16:37 00 [回复]举报

看建筑性质

关闭

关闭

手机APP下载