四层以上楼层设置歌舞娱乐放映场所需设置防烟排烟设施,具体要求是机械防排烟和自然防排烟都可以,还是必须设置机械排烟?

四层以上楼层设置歌舞娱乐放映场所需设置防烟排烟设施,具体要求是机械防排烟和自然防排烟都可以,还是必须设置机械排烟?

为梦而生 | 2024-05-07 22:42
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

消防检查 2024-05-08 08:43 00 [回复]举报

都可以,自然防排烟条件不具备再考虑机械。

小甜甜$$ 2024-05-08 12:39 10 [回复]举报

《建筑设计防火规范》8.5.3 民用建筑的下列场所或部位应设置排烟设施:
    1 设置在一、二、三层且房间建筑面积大于100m²的歌舞娱乐放映游艺场所,设置在四层及以上楼层、地下或半地下的歌舞娱乐放映游艺场所;



一纸荒年   回复: 小甜甜$$2024-05-08 14:58

排烟设施包括机械跟自然,只要满足条件任何一种都可以的!

0    1 [回复]举报

香.香 2024-05-10 11:54 00 [回复]举报

机械还是自然需要看该建筑的高度和使用性质,具备自然排烟条件可以设自然。反正同一防烟分区不能又机械又自然就行

蜗牛仔仔 2024-05-10 13:03 00 [回复]举报

优先自然排烟,但不允许同一区内和两个排烟方式

潘天坤   回复: 蜗牛仔仔2024-09-13 17:20

同一个防烟分区应采用同一种排烟方式,不同防烟分区不作要求

0    0 [回复]举报

潘天坤 2024-09-13 17:18 00 [回复]举报

规范要求在地下或半地下、地上第四层及以上楼层的歌舞娱乐放映游艺场所应设置排烟设施,排烟设施分为自然排烟设施和机械排烟设施,只要符合规范要求即可

不过要考虑每个房间建筑面积是否大于50平方米,每间房间是否有可开启外窗,走道是否具备自然排烟条件,走道两端可开启外窗面积是否符合要求,需要具体情况具体分析,综合考虑排烟方式