温控式七氟丙烷(悬挂式)灭火装置

温控式七氟丙烷(悬挂式)灭火装置,《消防设施通用规范 GB55036-2022》8.0.6 用于保护同一防护区的多套气体灭火系统应能在灭火时同时启动,相互间的动作响应时差应小于或等于2s(气灭规范也是如此)但现场温控玻璃泡咋能控制这个动作时间同时启动,火烧到哪才能喷,没烧到的不喷?如果不能的话,这个温控式只能单独设置?那这个装置设计出来岂不是很鸡肋?

炉边的风 | 2024-04-30 16:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

爱咋咋地 2024-05-01 23:09 00 [回复]举报

这个规范说的是有管道的,有气体瓶组和驱动气体瓶组的气体灭火系统吧?并不是你说的这种悬挂式的

一个消防路上的小学生 2024-05-03 15:48 00 [回复]举报

个人理解:通规和气灭规范所说的是当悬挂式灭火装置采用电启动方式时的要求时间。悬挂式气体和干粉灭火装置本就有多种启动方式。规范编制组不会不考虑楼主的想法的。谢谢

黄辉 2024-05-06 13:57 00 [回复]举报

温控式七氟丙烷(悬挂式)灭火装置,建议一个防护区只设置一套。如果需要设置多套,则应设置电磁型七氟丙烷(悬挂式)灭火装置,通过火灾自动报警系统联动控制同时启动。

按规范要求不需要设置自动灭火系统,只作为加强保护措施,可设置一套温控式七氟丙烷(悬挂式)灭火装置,比如电缆竖井中。

EHS专家-DL 2025-04-03 16:28 00 [回复]举报

《消防设施通用规范》第8.0.6条明确:同一防护区的多套气体灭火系统需实现‌同步启动‌,且动作响应时差≤2秒‌。该条款适用于所有气体灭火系统(包括管网式、预制式及悬挂式)‌。

温控式七氟丙烷悬挂装置‌不可直接用于需多套系统联动的防护区‌,其设计需严格遵循以下原则: 仅限单一装置覆盖的小型独立空间使用‌;大空间防护必须采用电控联动系统,通过火灾报警信号实现多装置同步启动‌。违反上述原则将导致系统失效及规范合规性风险。