幼儿园建筑的分班活动场地是否可以设置在三层屋面?

    幼儿园建筑,共三层,由于用地条件有限,无法在地面设置足够的儿童活动场地,请问是否可以将分班活动场地设置在屋面?屋面有2部疏散楼梯间疏散至地面。

001HXD | 2024-03-27 09:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

一路向西 2024-03-28 09:56 00 [回复]举报

相当于在

南明离火 2024-03-28 10:46 10 [回复]举报

4.3.4 儿童活动场所的布置应符合下列规定:
    1 不应布置在地下或半地下;
    2 对于一、二级耐火等级建筑,应布置在首层、二层或三层;
    3 对于三级耐火等级建筑,应布置在首层或二层;
    4 对于四级耐火等级建筑,应布置在首层。



不可 ,幼儿园儿童活动场所 只能设置在三层及以下

我已不是我   回复: 南明离火2024-03-29 17:46

如果三层屋面2部疏散楼梯是供屋面独立使用,且屋面耐火等级是符合要求的呢?建规里是把符合疏散要求并具有直接到达地面设施的上人屋面认为是室外安全区域的。

0    0 [回复]举报

南明离火   回复: 我已不是我2024-04-01 09:08

如果是这样设置的话,是否能够同理可证,把儿童活动场所设置在 33层高层建筑的屋面,屋面2部疏散楼梯是供屋面独立使用的。

0    0 [回复]举报

我已不是我   回复: 南明离火2024-04-02 17:06

嗯嗯,确实这样延伸类比就明显不合适了。改变了屋面的使用性质,不能简单认为是上人平屋面,而认为是室外安全区域了。

0    0 [回复]举报

我是小鱼鱼 2024-03-29 13:31 00 [回复]举报

江苏明确,不可