机械排烟,外门自然补风需要联锁吗?

最近一个项目,商场改造,机械排烟,利用外门进行自然补风,审图老师根据《烟规》第4.5.5条,要求外门与排烟系统联动启闭。电气说没有这种做法。我个人认为4.5.5条是机械排烟系统和机械补风系统应连锁启闭。如果有自然排烟系统或自然补风系统,就没有必要做联动。比如一个防烟分区采用自然排烟(手动)+自然补风(手动)是规范允许的?那何谈联动一说?

13911120083 | 2023-11-27 10:29
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

GANSTER 2023-11-28 16:22 00 [回复]举报

确实存在谁来打开补风口的问题,但4.5.3条规定又允许采用手动开窗开门的方式补风,个人意见:当补风口与排烟口位于同一防烟分区时可以手动,当分属不同防烟分区时宜采用连锁自动开启。

whale 2023-12-14 11:28 00 [回复]举报

河南这边刚出的文件