消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

安全出口设置

1、建筑设计防火规范 GB50016-2014 (2018年版):
3.8.2 每座仓库的安全出口不应少于2个,当一座仓库的占地面积不大于300m²时,可设置1个安全出口。仓库内每个防火分区通向疏散走道、楼梯或室外的出口不宜少于2个,当防火分区的建筑面积不大于100m²时,可设置1个出口。通向疏散走道或楼梯的门应为乙级防火门。
2、建筑防火通用规范 GB55037-2022 :
7.2.3 占地面积大于300m3的地上仓库,安全出口不应少于2个,建筑面积大于100m?的地下或半地下仓库,安全出不应少于2个。仓库内每个建筑面积大于100m2的房间的疏散出口不应少于2个。
3、请教下,2本不同的规范,说法不一致。我司有个项目是单多层戊类仓库(共4层),占地不大于300㎡,但4层楼为一个防火分区,防火分区的建筑面积大于100m²,这种情况下,是否还需要加建个室外钢梯作为安全出口呢?

立方 | 2023-10-11 18:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 2

我的是昵称 2023-10-12 10:28 00 [回复]举报

1.两本规范的写作方式不一样,但表达的意思是一样的,一个是正说,一个是反说。建筑设计防火规范是反说,不大于的意思就是等于和小于可以设一个安全出口或疏散楼梯,建通规是正说,说大于了就要设置两个安全出口,反之,还是小于等于就设置一个。

2.建筑设计防火规范里的是防火分区面积不大于100平时可设一个出口,建通规是建筑面积大于100平的房间出口不少于2个。防火分区和房间不是一码事,不能等同看待。

3.看设计图纸,建筑设计防火规范是图纸设计单位的消防设计依据。图纸上有就加,图纸上没有就不加.

申请 2023-10-12 14:16 00 [回复]举报

应该设,防火分区面积超100了

关闭

关闭

手机APP下载