花生油生产车间需要上自动灭火系统吗?前提条件是什么?

请各位老师帮忙解答,谢谢!

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 3

消防网友78337 2023-05-23 08:36 00 [回复]举报

花生油生产车间是灌装还是压榨及其它,没有具体工艺及产品资料如何确定火灾危险性,也就不能确定所需要的消防设施。

如果是灌装,无加热等工艺,生产火灾危险性是丙类,只在厂房是高层或地下厂房时,需要自动喷水灭火系统。


如果是压榨及其它,在工艺中有温度超过或接近油品闪燃点时,就需要根据具体情况,确定为甲乙类火灾危险性,然后按需要设置自动灭火系统。


建筑防火规范里没有强制花生油生产设置自动灭火系统。

安洪全 2023-05-23 08:46 00 [回复]举报

建筑防火通用规范 GB55037-2022

8.1.8 除散装粮食仓库可不设置自动灭火系统外,下列厂房或生产部位、仓库应设置自动灭火系统:    

1 地上不小于50000纱锭的棉纺厂房中的开包、清花车间,不小于5000锭的麻纺厂房中的分级、梳麻车间,火柴厂的烤梗、筛选部位;    

2 地上占地面积大于1500㎡或总建筑面积大于3000㎡的单、多层制鞋、制衣、玩具及电子等类似用途的厂房; 

3 占地面积大于1500㎡的地上木器厂房;    

4 泡沫塑料厂的预发、成型、切片、压花部位;    

5 除本条第1款~第4款规定外的其他乙、丙类高层厂房;    

6 建筑面积大于500㎡的地下或半地下丙类生产场所;    

7 除占地面积不大于2000㎡的单层棉花仓库外,每座占地面积大于1000㎡的棉、毛、丝、麻、化纤、毛皮及其制品的地上仓库;    

8 每座占地面积大于600㎡的地上火柴仓库;    

9 邮政建筑内建筑面积大于500㎡的地上空邮袋库;    

10 设计温度高于0℃的地上高架冷库,设计温度高于0℃且每个防火分区建筑面积大于1500㎡的地上非高架冷库;    

11 除本条第7款~第10款规定外,其他每座占地面积大于1500㎡或总建筑面积大于3000㎡的单、多层丙类仓库;    

12 除本条第7款~第11款规定外,其他丙、丁类地上高架仓库,丙、丁类高层仓库;    

13 地下或半地下总建筑面积大于500㎡的丙类仓库。

陈曲 2023-05-23 10:23 00 [回复]举报

参考建规8.3 可燃部位较多 且单层超1500或总面积超3000 需要装  我是这么理解的 仅供参考 