消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

住宅建筑首层或二层设置物管用房超过300平方米,建筑怎么定性?

住宅建筑首层或二层设置物管用房超过300平方米,建筑怎么定性?超过300平方米的文化 活动站?

富哥 | 2023-03-15 15:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

永锅 2023-03-15 15:59 00 [回复]举报

应按商业建筑要求设计。

张牙舞爪的张 2023-03-15 16:14 00 [回复]举报

你这种情况现实中太多了。验收的时候按商业服务网点验收,过了直接把防火隔墙敲掉,多个卡位合并成一家。这种情况本身就属于破坏防火分隔设施里的一种,没法改。

富哥   回复: 张牙舞爪的张2023-03-16 08:25

有人说,这种物业管理用房是属于“”是社区公共用房,大多不计入建筑面积(当然有的开发商公摊了),它既不属于商业服务网点,也不是住宅,应定性为社区服务用房。“”而这种用房,他们认为面积超过300平方也没有问题,可以不按商业服务网点来定性,也不会改变建筑定性,这一点我总感觉有问题,但又说不出问题在哪。查规范又没有相关的对应的条文。

0    0 [回复]举报

富哥   回复: 张牙舞爪的张2023-03-16 08:30

张总,按您的意思,是不是在超过300平方时,用一道隔墙暂时来分隔,等验收后再拆除,那这意思也就是说,物业管理用房仍然是按商业服务网点来定性。那住宅中的活动中心这种情况应该怎么办?它的面积也是超出300平方的,也要这样用隔墙暂时分隔起来吗?

0    0 [回复]举报

张牙舞爪的张   回复: 富哥2023-03-16 12:04

商业服务网点特点是存在经营性质,这种公共活动用房严格来属于公共活动场所。建议问一下当地住建验收部门或消防部门。

0    0 [回复]举报

富哥   回复: 张牙舞爪的张2023-03-30 15:23

谢谢

0    0 [回复]举报

李勤 2023-03-16 11:46 00 [回复]举报

大于这个面积或不是类似使用性质,就不能算作商业服务网点。

关闭

关闭

手机APP下载