消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

耐火等级一二级公共建筑相邻防火分区借用疏散

在同一防火墙上设置了符合国家标准的防火卷帘,再设置符合国家标准且净宽度符合要求的甲级防火门,能否适应借用疏散的条文?
消防网友52121 | 2020-11-17 15:05
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

刘丽波 2020-11-18 12:16 10 [回复]举报

详见《建规》5.5.9-1条,借用的时候,通向相邻防火分区的墙上不能设置防火卷帘。应该是防火墙加甲级防火门的形式。

消防网友52121   回复: 消防网友52182020-11-18 23:56

20年技术实务真题单选69题看下应该选哪个?

0    0 [回复]举报

刘丽波   回复: 林@@2020-11-22 08:15

0    0 [回复]举报

刘丽波   回复: 消防网友52182020-11-22 08:16

您说的是此题吗?,正确答案选B

0    0 [回复]举报

消防网友14591   回复: 刘丽波2022-03-25 18:29

C选项有瑕疵,借用宽度不超30%,5.5.21除剧场、电影院、礼堂、体育馆外的其他公共建筑,其房间疏散门、安全出口、疏散走道和疏散楼梯的各自总净宽度,应符合下列规定:7.商店的疏散人数应按每层营业厅的建筑面积乘以表5.5.21-2规定

0    0 [回复]举报

关闭

关闭

手机APP下载