预作用报警阀压力读数

我公司是干式系统,预作用报警阀最近发现存在故障,维修完成后测试发现可以喷水,但是预作用报警阀压力全部是0,这种状态正常吗,正常的压力读数是多少,恳请各位老师指导一下,谢谢

消防小白000 | 2022-09-20 11:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

枫叶的孤独 2022-09-20 13:08 00 [回复]举报

肯定不对,系统侧要充低压气体用于检测系统漏气,供水侧要符合建筑高度要求的压力


枫叶的孤独 2022-09-20 13:09 00 [回复]举报

在有干式系统,不应该用预作用阀组啊 ,有干式阀组啊 。