某石化厂中控室的低压配电室配置了两具3公斤的水基灭火器,灭火级别为1A,55B,E。按照火灾危险性,中控室的配电间应该为严重危险级。

想请问E类场所,严重危险级,配备3公斤的水基灭火器符合要求吗?

谢谢

Chris_EWE9 | 2022-08-18 22:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

周家斌 2022-08-19 08:24 00 [回复]举报

消防网友68723 2022-08-19 10:40 00 [回复]举报

石油化工企业设计防火标准 GB50160-2008(2018年版)8.9.1 生产区内应设置灭火器。生产区内配置的灭火器宜选用干粉或泡沫灭火器,控制室、机柜间、计算机室、电信站、化验室等宜设置气体型灭火器。

消防学前班 2022-08-20 09:01 00 [回复]举报

按标准觉得应该配推车二氧化碳了,严重危险级手提式的二氧化碳达布到