消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

双联锁预作用,爆喷头后,供气管路低压压力开关动作压力是?

大神们,

双联锁预作用,爆喷头后,供气管路低压压力开关动作压力是多少?

crow0769 | 2021-12-08 21:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

宋福亮 2021-12-09 17:10 10 [回复]举报

根据《自动喷水灭火系统设计规范》5.0.17 利用有压气体作为系统启动介质的干式系统和预作用系统,其配水管道内的气压值应根据报警阀的技术性能确定;

       个人感觉:还得看探测器啥反映。1.如果是喷头损坏了排气,报警后人员检修,空压机(气泵按厂家设定值补气)启动补压。2.如果着火了,2个探测器动作---一路去控制器一路打开电磁阀和快速排气阀排气排压关闭气泵---管道排气冲水(干式变湿式)-----喷头破了就直接喷水灭火。


      个人思路,希望有用。

crow0769   回复: 宋福亮2021-12-09 18:50

非常感谢。有启发。


现实中一座保鲜温度0~4度冷库内,釆用由火灾自动报警系统报警与喷头爆破降气压作为预作用联动启动信号,在冷库内一个10平方米左右隔间内,有一个感烟火灾探测器,有一个末端试水装置,检测时吹烟、开阀,预作用控制箱2分钟后仍未收到联动启动信号。联动控制器自动且功能正常。


判断供气管路上低压压力开关设置值偏低。应设多少呢?


预作用系统近系统端的单向阀阀瓣上、下分别是:上为空压机0.03~0.05MPa有压力气体加水封、下为未知圧力空气,上泄压至0,也不会致阀瓣开启。所以,与干式的启动方式不同。


0    0 [回复]举报

刘丽波   回复: 宋福亮2021-12-11 08:35

不同设备厂家要求略有不同,以说明书为准。下边是两个产品说明和国标图,可以参考。


1    0 [回复]举报

crow0769 2021-12-11 15:30 00 [回复]举报

感谢大神!此惑己解。

关闭

关闭

手机APP下载