七氟丙烷系统按下“紧急启动按钮”时,是否会有30s的延迟

七氟丙烷系统按下“紧急启动按钮”时,是否会有30s的延迟

空中 | 2025-04-10 11:13
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

EHS专家-DL 2025-04-10 11:38 00 [回复]举报

七氟丙烷系统按下紧急启动按钮后‌存在可调延迟(0-30秒)‌,具体时长由系统设定决定。

树人 2025-04-10 11:48 00 [回复]举报

一般厂家出厂是会有30s的延迟,但是可以设置0-30s,但是一般建议不要动,因为按下启动按钮会一直报警,这30s是让人撤离,七氟丙烷还是有部分毒害的

消防网友70233 2025-04-10 12:24 00 [回复]举报

可以不需要。规范中规定了自动启动时,有人工作场所,有30s的延迟。到了机械应急启动模式时,基本属于确认火灾已经形成,该疏散的已经疏散,紧急启动不应设置延迟


消防资源网 2025-04-10 12:29 00 [回复]举报