多功能厅设计有1713座百人疏散宽度

请教一下各老师,一个多功能厅设计有1713座,请问百人疏散宽度是否是1713/100X0.75=22.8m,对吗?谢谢指教一下。

好叭 | 2025-03-03 23:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

小唐12321 2025-03-04 09:08 00 [回复]举报

是的

消防网友68723 2025-03-04 09:23 00 [回复]举报

有固定座位的场所,其疏散人数可按实际座位数的1.1倍计算。

小唐12321   回复: 消防网友687232025-03-04 09:53

应该不用,这个算礼堂,不属于其他。地方标准另外算

0    0 [回复]举报

LHH2737 2025-03-04 09:50 00 [回复]举报

是的

但要注意,如果同时具有电影院功能时,个别地标,比如浙江规定:其疏散人数应为影厅内座位数、工作人员数和候场人数之和,每层候场人数应按该层各厅平均座位数且不小于该层各厅总座位数的 20%计算。