自带蓄电池应急照明灯安装时的问题

自带蓄电池应急照明灯都带有插头,安装正确位置上,是不是可以直接插入插座就可以了。

淡定119 | 2025-02-26 16:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

赖峰 2025-02-27 08:15 10 [回复]举报

不可以,插头与插座之间应采取采用专用工具方可拆卸的连接方式连接。
应急照明属于消防设备,必须确保在火灾等紧急情况下持续供电。普通插座可能因插头松动、接触不良或被误拔而导致断电,影响应急功能。



消防应急照明和疏散指示系统技术标准 GB51309-2018

第3.3.2 应急照明配电箱或集中电源的输入及输出回路中不应装设剩余电流动作保护器,输出回路严禁接入系统以外的开关装置、插座及其他负载。

4.5.5 非集中控制型系统中,自带电源型灯具采用插头连接时,应采用专用工具方可拆卸

小唐12321   回复: 赖峰2025-02-27 09:16

但是现实就是你买不到专用插座,然后市场上这些产品合格吗

0    0 [回复]举报

小唐12321 2025-02-27 08:22 00 [回复]举报

规范专有插座,现实很多都是。

龙心 2025-02-27 16:22 00 [回复]举报

不用插头,直接接电,专用回路。