消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

剪刀梯公用前室里面设置水电井这样可以吗?

建规5.528  楼梯间的共用前室与消防电梯的前室合用时,合用前室的使用面积不应小于12.0m2,且短边不应小于2.4m。我可以这样设置水电井吗????


洋仔啊 | 2025-02-15 12:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 2

小唐12321 2025-02-17 08:22 00 [回复]举报

5 除住宅建筑的楼梯间前室外,防烟楼梯间和前室内的墙上不应开设除疏散门和送风口外的其他门、窗、洞口。

老李不老 2025-02-18 09:59 10 [回复]举报

公建的楼梯间和前室都不能设置管道井的门,依据见楼上。另外,还需要注意,上图瓶颈处净宽不足1.2米(考虑抹灰后),不满足《民用建筑通用规范》5.3.12条:除住宅外,民用建筑的公共走廊净宽应满足各类型功能场所最小净宽要求,且不应小于1.30m。

关闭

关闭

手机APP下载