多层建筑内设置夹层的问题

在多层公共建筑的二层设置夹层,夹层面积不超过200平米,功能为排烟机房和库房,能不能只设一个楼梯。

lyh | 2024-11-16 18:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

jinyanwu 2024-11-18 11:01 00 [回复]举报

根据通规,多层公共建筑内只设一个楼梯的只能是如下情形:

水流岚 2024-11-19 10:35 00 [回复]举报

不行,不超200平米单独设置一把疏散楼梯的情况有两种

1、50016-2014中,5.5.5条规定的地下./半地下设备房

2、50016-2014中,5.5.11条规定的局部升高出屋面的多层公共建筑

你说的情况不属于以上两种,不能只做一把楼梯

shwbest 2024-12-02 15:18 00 [回复]举报

如防火分区面积叠加夹层面积后不超规范要求,且《建筑设计防火规范》GB50016-2014第5.5.8条规定了公共建筑安全出口设置的原则要求:第5.5.17条对公共 建筑的安全疏散距离按照平面布置的不同情况作了相应规定。当 公共建筑内的夹层与下部楼层为同一防火分区,夹层内未设置疏散出ロ、人员需经下部楼层设置的硫散出口疏散时,夹层内的任一点至疏散口的疏散距离应满足第5.5.17条第3款的规定。其中经楼梯从夹层疏散至下部楼层的距离应按其梯段水平投影长度的1.5倍计算。