消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

柴油消防泵输油管线有无具体要求,或者明确使用何种材质,因在规范里找不到对应的标准

柴油消防泵输油管线有无具体要求,或者明确使用何种材质,因在规范里找不到对应的标准

消防网友34100 | 2024-11-12 08:34
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

喧哗 2024-11-12 11:05 10 [回复]举报

我见过的柴油泵输油管路是塑料软管的,那两个白色的软管就是,但是现场柴油泵是后改造的,我觉得不太好,因为可能会有高温。输油管路在SH/T3219-2022 9.2.6规定可采用碳钢、不锈钢,不应选用铜、铅、锌等有色金属成分的材质。

懒得说 2024-11-13 16:59 00 [回复]举报

规范好像没有明确要求。实际操作用过热镀锌钢管和铝塑复合管

消防网友49840 2024-11-14 13:44 00 [回复]举报

我们现场用的是金属编织层高压软管(金属编织层单端做接地)

关闭

关闭

手机APP下载